Not exactly correct skidmark you can lay them in a trench as long as it is at least 30" deep. Here is the code..250.56 Resistance of Rod, Pipe, and Plate ElectrodesA single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(2) through (A)(7). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8 m (6 ft) apart.The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.All rod and pipe electrodes must have at least 8 ft of length in contact with the soil, regardless of rock bottom. Where rock bottom is encountered, the electrodes must either be driven at not more than a 45-degree angle or buried in a 2 1/ 2-ft-deep trench. It should be noted that driving the rod at an angle is permitted only if it is not possible to drive the rod vertically to obtain at least 8 ft of earth contact. Burying the ground rod is permitted only if it is not possible to drive the rod vertically or at an angle.Ground clamps used on buried electrodes must be listed for direct earth burial. Ground clamps installed aboveground must be protected where subject to physical damage.
This is CABL.com posting #324007. Tiny Link: cabl.co/mbwr5
Posted in reply to: Re: 10 ft. Ground Rod Installation Helpful Ideas by skidmark
There are 0 replies to this message