830.106 Grounding and Bonding at Mobile Homes.
(A) Grounding. Grounding shall comply with 830.106(A)(1)or (A)(2).(1) Where there is no mobile home service equipment located
within 9.0 m (30 ft) of the exterior wall of themobile home it serves, the network-powered broadband
communications cable, network interface unit, and primary protector ground shall be installed connected to a
grounding conductor in accordance with 830.100(B)(2).(2) Where there is no mobile home disconnecting means
grounded in accordance with 250.32 and located within sight from, and not more than 9.0 m (30 ft) of,
the exterior wall of the mobile home it serves, the network-powered broadband communications cable,
network interface unit, and primary protector ground shall be installed connected to a grounding conductor
in accordance with 830.100(B)(2).
(B) Bonding. The network-powered broadband communications cable grounding terminal, network interface unit
grounding terminal, if present, and primary protector grounding terminal shall be bonded together with a copper
bonding conductor not smaller than 12 AWG. The networkpowered broadband communications cable grounding terminal,
network interface unit grounding terminal, primary protector grounding terminal, or the grounding electrode
shall be bonded to the metal frame or available grounding terminal of the mobile home with a copper bonding conductor
not smaller than 12 AWG under any of the following conditions:
(1) Where there is no mobile home service equipment or
disconnecting means as in 830.106(A)
(2) Where the mobile home is supplied by cord and plug